To see if a motor encoder is sending feedback signal, I put multimeter leads on the A & A- encoder wire terminals (same thing on the B & B-), then turn the motor shaft. I just assume the encoder is good when I see some voltage reading changing.
Is there a better way to check the encoder with a mumtimeter?
I would use an o-scope and look at the signals. you should get a nice square wave. the a and a- are differential as is the b and b-. the a and b channels will be offset by 90 degrees.
A multimeter will show something, but nothing useful. You might set it to read frequency, and verify if the frequency is correct for a given speed.
That still misses channel phasing, and pulse quality.
An Oscilloscope would be much better, like this, but seriously, an encoder tester like this one is the way to go.
Failure modes for encoders are missing output, and weak LEDs. Phasing is fixed - no need to measure it.
The following is for a 5 volt TTL output version.
Multimeter will show that you have two outputs. Next, check for switching between zero and 5 volts. With weak LEDs, these voltages will be way off.
The other thing you can do is test on the machine. Do this test away from the home position, in case the machine resets the counter at home.
Move 1000 counts positive, then 1000 counts negative. Repeat 10 times. Is the count still accurate? With weak LEDs, or slipping mechanics, this count will be off.
Modify procedure for your machine.
An oscilloscope or encoder tester is still the best method.
Hi all, i want to check incremental encoder ppr using oscilscope. how can i check ?
2,184
Hi All, i have one incremental encoder use postion decoding of travsing purpose in siemens S5 plc.now proper postion of travsing not detected by...
5,719
Hello, can someone share/explain How to check comms between PC and PLC via TeamViewer? TIA
400
Hello, I have a question on an OCR application I am doing. I am reading in 16 characters that come from a camera into the plc in its input words...
1,282
I have some questions about MSG Type checking Does a MSG instruction care if the name of the UDT type are different on each PLC as long as...
3,471