All,
I have a 24VDC/10A Power supply feeding a bunch of sensors and field devices.
Since I don't know the total Amps already being used by their documentation, can I check the total ohms by disconnecting the PS and then use Ohms law to figure out the total A? I know you can't do this on AC systems because inductance.
Thanks!
if the power input of these devices were simple resistances or coils probably measuring the resistance could work, but most now days devices have internal non-linear switching power supplies, for example those that allow a wide range of input voltage, then to measure resistance and apply Ohm law will not work.
The only solution for me is to connect a 24DC source and measure the intensity.
Apart from the above, if there are incandescent lamps the resistance measure can also be very inaccurate since they have much less resistance when they are cold.
You can start by using the device data to do a load calculation. Most suppliers give numbers that are worst case, so it should give you some indication of what the total demand on the PS will be.
may be the power input of these devices were simple resistances or coils probably measuring the resistance could work,do you think so.
No. See post #4.
Connecting the Fluke is easy. I don't understand why we're looking for a harder way to do it.
Hello, can someone share/explain How to check comms between PC and PLC via TeamViewer? TIA
395
Hello, I have a question on an OCR application I am doing. I am reading in 16 characters that come from a camera into the plc in its input words...
1,282
I have some questions about MSG Type checking Does a MSG instruction care if the name of the UDT type are different on each PLC as long as...
3,469
I just finished making my 3rd service call to a large machine shop, troubleshooting PLC issues. I can see that none of the PLC or HMI programs are...
3,074
All of these processes are taking all day to run. When doing the same operation in a stand alone intouch application it only take a few minutes to...
1,613