Cimplicity Alarm Class Configuration

Eugene_k510

Member
Join Date
Jan 2020
Location
Malaysia
Posts
8
Hi, im facing an issue to change the alarm level into another state in the alarm class configuration in Cimplicity.

Im trying to change the alarm level from "HiHi" to "Hi", and every time i hit apply the configuration goes back to the original state which is "HiHi"

Is there anyway where i can change the settings ?
 
Hi, im facing an issue to change the alarm level into another state in the alarm class configuration in Cimplicity.

Im trying to change the alarm level from "HiHi" to "Hi", and every time i hit apply the configuration goes back to the original state which is "HiHi"

Is there anyway where i can change the settings ?
Hi,
The alarm level is not a value or setting you can change. It is the item you select to change its foreground and background. After you close the dialog and reopen it, the alarm level displays default selection which is hihi.
Try to change foreground or background of any alarm level, hit ok then reopen the dialog, you will see the change for that alarm level has been saved.
 

Similar Topics

Hi! Good day everyone! This is my first time posting here at PLCS.net and I need some help on how to make a group of alarms, displayed...
Replies
2
Views
1,770
Dear Experts!!! We are working on GE Cimplicity 9.0 SCADA which is communicating with Siemens S7 400H PLC System. I am new to Cimplicity SCADA...
Replies
2
Views
3,032
I have a project ,it need View a CimView screen through the Alarm Viewers; Select the Alarm ID when the point is in Alarm State and appears in the...
Replies
0
Views
1,861
Hi All, I am new user of Cimplicity, i am trying log alarm but in alarm viewer i can see alarm is working but it is not logging in hostorical...
Replies
2
Views
5,964
Is it possible in Cimplicity Version 8.20 to export the alarm classes to a csv file similar to the Clie database export??
Replies
4
Views
3,563
Back
Top Bottom