Hi All
I'm trying to add an analog input module to my Click plc to attach some potentiometers to. I can't seem to get any data in my system monitor window. it's all reading 0.0 mA. I did go through the configuration to make sure the computer was reading it. I Don't have any LED lights in the module turning on but my Normal PLC is working just fine with reading data inputs. I don't think there are any LED lights on the actual board.
I have a C0-00dr-0 with a C0-04AD-1 module attached.

any advice?
 
I have wired it to the 24v and the 0v on the 2 bottom (lowest in the set) connections of the module. I also have a wire going to the channel 1 from the potentiometer which I get a voltage signal from. I still get a reading from the computer that I have 0 mA
 
I also have a wire going to the channel 1 from the potentiometer which I get a voltage signal from. I still get a reading from the computer that I have 0 mA

HMMM?

The C0-04AD-1 is a current input module not voltage.

If you connected 10 volts to the input you may have damaged the input. See pdf below.

Input impedance is 124 ohms, with 10 volts's connected gives you 80 ma. Max is 44ma (not good)

https://www.plcdirect.eu/downloads/...tasheets-3/301-datasheet-click-c0-04ad-1/file
 
Last edited:
C0-04AD-1 is a current input module. Input Impedance is 124 Ohms. That sets it's voltage input from 0-2.48 volts. Not going to work with a pot input. You need C0-04AD-2.
 

Similar Topics

I need to change my program to increase a IP transducer by 0.5 psi every 5 seconds. I am making a automated pressure tester using a pump, IP...
Replies
6
Views
1,054
Click Plc/analog 0-10 v output module/0-10v dimmable led driver. I made a program using multiple drum to create by increment fade in and out led...
Replies
3
Views
1,412
Hi all I am trying write a program that has analog input from a pressure sensor in a tank that read the pressure sensor for level when the pump...
Replies
12
Views
6,587
I'm reading Modbus data over TCP from a remote I/O device with an HMI. i'm reading it into an UNSIGNED INTEGER tag Modbus 40001 = Input 1 Modbus...
Replies
2
Views
1,934
I have an Automation Direct Click PLC (C0-02DD2-D) with a 24 VDC power supply. I want to make a variable input device to supply the analog input...
Replies
2
Views
3,677
Back
Top Bottom