CLX I/O Configuration: "Assembly Instance" ??
theDave2
Aug 2004
Rochester, NY
467
What the heck is "Assembly Instance " ? I see that I have to fill it in when using a HiProm Profibus gateway.
I don't see any AB help about it. And searching the 'net doesn't reveal anything relevant.
On a side note: for this profibus-PA device, it needs a REAL tag (for the Process Variable) , but only DINTS show up when defining the communications format and in the I/O controller tags when the Gateway is defined. Is there a way to coerse a DINT to a REAL?
The required assembly instance values should be provided by the module's manufacturer. They are the 'Raw' way of telling the Logix processor how to format communications to the module. With AB or actual defined modules with full EDS Files, most of that is hidden behind the scenes.
As far a data formats go, depending on endian-ness (Byte Ordering), you might just be able to do a block copy (COP) from the DINT array to an array of REALS (of the same size). Both datatypes are 32 bits, and COP doesn't care about the source and destination data as long as there is room in the destination array.
If you have an endianness problem, then you will either have to try to get the gateway to 'play nice', or you will have to byte swap the pieces of each 32 bit DINT until you get the right endian format to copy to a REAL.
But which manufacturer ? AB CLX, the profibus gateway or the profibus instrument ? The only place I see it called out is a screen shot by the profibus gateway company.
There are 3 entries: Input, Output & Configuration.
Thanks for the COP hint, I'll try that.
The Profibus gateway company. The instruments have nothing to do with the interface to the Logix backplane, and the CLX only needs the assembly instances (which generally correspond to the ":I, :O, and :C" entries in the tag table) in order to talk to the module.
"Assembly Instance" is the pointer to a specific memory location within a device that supports CIP. These numbers are device specific. Only device manufacturer can provide this.
I agree that "Assembly Instance" is not very descriptive for electrical engineers who typically program PLCs, but looks like most of CIP specification written by "C" programmers and "object oriented" thinking is normal for these guys.
I do 'C', I do 'OOPS', I never heard of it before now.
BTW, I did use a COP and that did 1/2 the trick. The other 1/2 was finding out that the PIT display reads out in PSI but the Profibus was sending the pressure in BAR.
Tsk Tsk!
C is definately not an OO design language, that's what C++ is for, which is actually a similar, but very separate language (Not just an extension to C, in other words).
Need a little help if you please! Current situation: PLC 5/80E whose firmware doesn't support messaging. It currently has about 18 1336/1305...
2,604
In a 1756 Controllogix(CLX) chassis there is a SST Profibus module, i have the configuration Software for CLX but do not know or have the...
6,772
Hello everybody, I am working with a ControlLogix 1756 L63 controller and RIO, with a DHRIO module. I have a doubt about the Cache Connections...
3,721
I have 2 SST-PFB-CLX modules (Slot3 and Slot6) in my 1756 A/B PLC. Both modules are working O.K. I tried to upload actual configuration using SST...
1,728
I have a SST Profibus Module In a CLX. Which works fine, I need to add a slave to Profi ring, I have the PBC file from the OEM which matches the...
4,592