Just a thought that the BTW may be failing because the Channel Min and Max Scaling parameters are all set to zero in the configuration BTW data ??
Is this not fine to use as a standard setting?
Just a thought that the BTW may be failing because the Channel Min and Max Scaling parameters are all set to zero in the configuration BTW data ??
Gather the Series letters and part numbers of everything, including that power supply. Note the DIP switch settings both on the 1771 backplane and on the 1771-ASB module.
The initial IFE card that was in my set up was infact a IFE/A rev C so I was a little confused. I now have replace this with and IFE/C.
No longer getting that same error.
Now the only final thing is where do I set my pointer for the data?
Is there a way that I can test it internally/theoretically. Type a number somewhere and make sure that it is reading that?
I am not all that great when it comes to physically wiring PLC's to the inputs and outputs we have electricians out here that do that work for me
Thanks for the help again
ok so you are required to use the BCD format and not just a decimal.
I see that without a swing arm my input module was already reading a value of 1053 and 1616 on the first 2 channels
whenever we humans look at the BCD scaling data value 4095 in DECIMAL form (the default numbering format for most of our newer systems) we see the number 16533 ...
so ...
as long as you keep your data table format set up for "decimal" you can just type the data in as 16533 – secure in the knowledge that when that same data gets written into the IFE module, the module will interpret/accept/recognize the data value as 4095 ...
You are a smart guy
I was not meaning this to be insulting your intelligence in anyway
I know that some not as versed in logic/binary read these as well and was just providing extra information for those who don't know.