Hi everybody.
I connected SLC 5/05 via Ethernet to Logix 5561, using Network switch, Logix5561 communicate via 1756ENBT Eneth/Ip adapter
rslinx view:
MSG Instruction setup, here you can see logic too, I not sure is it right, I took it from working unit
Maybe somebody know what the problem is, I don have any data from slc
From what I can see, all appears to be configured OK.
Can you attach your 5561 program and your SLC program (Zip them first) we can investigate further...
Explain what you mean by "I don't have any data from SLC".
Does the /DN bit for the MSG control tag come on ? What about the /ER bit ?
What is the value in the SLC's data table for "N7:0" that you expect ?
While the SLC can respond to both PLC-5 and SLC-500 commands, you might want to change the message type to SLC Typed Read instead of PLC-5 Typed Read.
Does the L61 have a SLC mapping table set up?
It doesn't need one, the MSG instruction's destination tells the processor where to store the data.
Mapping is only needed for Reads and Writes initiated by a PLC that doesn't support ControlLogix tags (i.e. older machines).
Hello. I am in the process of designing a new project and I was able to successfully go online with the SLC 5/03 using a 1746-UIC cable through...
1,494
Hi, I have a machine with AB SLC 5/05 PLC and it already has its “Ethernet” port utilized for plant network. Now I'm designing one more panel...
2,803
In my case I was having panelview900 connected to SLC 5/03 through DH485 using AIC+ Advanced Interface Converter (1761-NET-AIC), an Isolated Link...
1,825
I have 2 SLC500/04 The master has it´s own I/O The slave has it´s owns I/O if master has an Input on, i want the slave turn on an Output. how...
4,903
Several months back we installed a Red Lion G315 HMI to communicate with a AB SLC 5/03 attached to the ethernet network via an AB ENI module...
4,487