i am facing problem to communecate omron PLC CJ1G- cpu44H with Pt NT31C Ev2 when we try to communicat Pt dispaly (program Initializing) and dont open program i m using Method PLC > convertor RS232 To Rs 422A > To PT NT31c Ev2 Port B
 
i am facing problem to communecate omron PLC CJ1G- cpu44H with Pt NT31C Ev2 when we try to communicat Pt dispaly (program Initializing) and dont open program i m using Method PLC > convertor RS232 To Rs 422A > To PT NT31c Ev2 Port B

Is this an existing setup, or a new installation? What Communications Protocol are you using between the PT and PLC? Which Port on the CJ1G? What RS232 to RS422 Converter are you using? Perhaps the best bet would be to post your PLC and PT Programs.

A common mistake I have seen is the RS422 wiring. The Send Pair must be connected to the Receive Pair at the other end. I have seen Electricians wire them Send to Send, and Receive to Recieve. Guess what, no communications.

Stu.....
 
plc to pt communicat problem

This is an existing system ant me only reprogram this system on pt nt31c pfrom plc RS232 and then in converter because my wire lenght is near about 20 mtrs between plc and pt from convertor RS422A to Pt Port B

090320103943.jpg
 

Similar Topics

Hi all. I have a Modbus ProSoft module in my setup with a capability of 30 clients (0-29), which I'm trying to monitor the Ethernet Connection...
Replies
0
Views
31
Hi folks, I have a Controllogix in communication with a zigbee coordinator using Logix AIO for modbus tcp. This zigbee coordinator have 3 slaves...
Replies
6
Views
161
Hello, i am using profibus as communication between plc and fanuc arm. I can easily send inputs from plc to arm, but i can't monitor any outputs...
Replies
0
Views
45
I have Woodward Controller EASYGEN-3500XT and Phoenixcontact make IO CAN-CUPLER part no: 2702230, Analog Input card: 2861412, Analog Output Card ...
Replies
0
Views
47
Hello Everyone, I have a issue with communication between two different PLCs. So here is the facts, The Master PLC is Guard Logix 5069 with IP...
Replies
4
Views
110
Back
Top Bottom