CompactLogix integration with InTouch 8.0

bevan.jones

Member
Join Date
Mar 2005
Posts
1
A client has specified AB Compactlogix L35E and WW InTouch 8.0, they want to use Ethernet I/P for I/O and Scada. Has anyone used these this combination without a third party I/O Server? If so, how?
 
The Wonderware DASever "ABTCP" I do believe will do the trick. In documentation they only mention ControlLogix, But I have successfully implemented it with a FLexLogix PLC, and am pretty sure it will work with the CompactLogix line as well.

It is free, so it is hard to go wrong with trying it out.
 