Compactlogix reading SLC/Micrologix fault
Dariusincj
Jul 2011
Missouri
43
I'm attempting to read about 5 different PLC's and storing their data in a CompactLogix 5380 where I can manipulate the data I need. I am having issues setting up the message block.
I've got the message block setup in the CompactLogix to connect to the micrologix 1400 but i'm getting Parameter error in module configuration. It's set as a SLC Typed Read, source element N201:0, number of elements 1, and my destination is an INT.
The other SLC's on the AB-X2-ABDHP, i'm not even sure how to set up the communications on those.
Anyone ever try to do it?
Is that a view from RSLinx, or the I/O tree of the CompactLogix ? I guess you're connected to the CompactLogix over USB and are browsing the network.
Be sure the MicroLogix is not in the I/O tree; that can interfere with its comms because it cannot create an I/O connection and will get confused by the repeated attempts to establish one.
What is the exact error message in your MSG instruction ?
That is a screen shot of the connections in Linx, from USB connection. I have nothing in my I/O config tree in the PLC. With the micrologix message I'm getting a Parameter error in module configuration error message.
What type of SLC is connected to the AB-X2-ABDHP, and through which port ?
MSG instructions to controllers on DH+ are actually aimed via the CIP path to the DHRIO module, and then processed by the DHRIO module on DH+.
Read up in the MSG Help on how to configure the message so it gets to the DHRIO, from which point you tell it which port and which node to execute the message on.
Can you screenshot that, as well as the configuration of the MSG instruction ?
What is your exact CIP Path to the MicroLogix ?
For messages to the SLCs on the DHRIO module, refer to this thread for a similar example:
http://www.plctalk.net/qanda/showthread.php?t=112454
That example is ControlLogix, with the route going out of an Ethernet module rather than an integrated Ethernet port on the CompactLogix. So it will not be an exact match.
I did use that link, set it up. Now I have the same error on that message block as I do with my Micrologix message block. Not sure why though.
I'm striking out...but I have to ask: L7_SYSTEM is an array of type INT in the CompactLogix? No typo?
Everything looks OK to me.
I've never seen N files in the 200 range for a micrologix.
Try to read N7:0 and see if that works? Like others, I am grasping at straws here. But the SLC typed read likely has some artificial limits, given when it was designed.
Here is my code, reading a Micrologix 1100 from a ControlLogix L73, working as it should
Thanks for posting those error codes, and especially because you posted that RSLinx Browse at the beginning.
The problem is very likely the CIP Path.
The 5069 CompactLogix has a feature that other controllers have never had before; the ability to either use the two Ethernet plugs as one port or as two.
When you set it up so that they're one port, they get one IP address and you can use the DLR ring feature.
When you set it up so that they are two ports with different IP addresses, you can't use DLR but you can set the two Ethernet plus up for different IP addresses.
AND... the outgoing CIP Port number changes. In 1-port mode it's CIP Port 2. In 2-port mode, they are CIP Ports 3 and 4.
Try changing your CIP Path to "4, 192.168.0.40".
Hi everyone, Brief overview of the issue: I have a CompactLogix (pt No:1769-L36ERM) that is connected to a MicroLogix 1400 (Pt no: 1766-L32BXB)...
4,308
Hi again guys, This forum has been great for all the questions ive asked these last few days. Another one now.. haha I am currently working...
4,220
Quick version is is it possible to read the language that the user has selected on a Panel View? There seems to be no system flags but are there...
4,132
I have a small network setup to read and write between a CompactLogix L32E and a Micrologix 1500 LRP via a NET-ENI. I can send data to the...
5,804
Hi All, I'm just trying to understand the reason behind something I recently experienced. Background: The system contains 4 CompactLogix...
128