Forum,

I am parag from India working on Triconix systems. in this i am right now doing Programming for Some of the compressore. But I have never came across of Compressor Loading & Unloading Philosophy.
Compressor Loading is 0%,25%, 50%, 75% & 100 %.

Please help me how its functionality if anybody already came across of these Philosophies.

Thanx in advance.

Parag Uike
(The Game Of PLC +++)
 
to avoid stopping and starting of compressors you can switch off 100% and 75% of the first compressor before stopping the second.
so when stepping up do normal and when stepping down step down second until 25% then step down first to 75% then step down to 50% and if still too much stop second compressor.
in air systems use a bigger tank and in cooling systems use other limits to have it running smoother.
 

Similar Topics

we are controlling the unloading and loading of two instrument air compressors using a SCP BLOCK/ SCL500 system. 4-20MA OUTPUT VIA A I/P WHAT IS...
Replies
11
Views
2,292
There are two solenoids to control a screw compressor slid valve; one is for Load and the other one is for Unload. I would like to control the...
Replies
0
Views
4,756
I Am looking to get ahold of the modbus map for an air compressor. I HAve emailed the vendor as well, just wondering if any of my friends here...
Replies
1
Views
120
Got a customer with a Chinese air compressor, 240V, 15HP. The present control of the entire system is inside their VFD. It controls the motor...
Replies
2
Views
1,059
Hey All, I've got a Sullair LS-16 (V160) compressor with the 3-line Supervisor controller (identical to this...
Replies
9
Views
2,473
Back
Top Bottom