Comunication HMI and PC

ja_varela77

Member
Join Date
Aug 2013
Location
Petaluma
Posts
5
Hi

Regards to all people.

I bought a HMI Red Lion G304K200. I installed the Crimson 3.0 in my PC and I made the cable PT# BLPRO4K (serial cable).

I have problem with the comunication between the PC and HMI.
Only the first time that connected the HMI to PC (in serial mode), I achieved transfer only a screen to test. Now, I dont know that happen, I cant transfer and show the next message "Error. - No there arent acknowledgment from the destination equipment".

I need your help please.
Thanks.
 
What did you transfer ? what are the LED's doing anything? (flashing)

You can also try this.... It should set it back to factory default and clear your program

redlion34251.jpg
 
Thanks brother

I followed your advice and reset the HDMI. Now I can transfer in mode serial.
Thank you very much for your support.

Regards.
 

Similar Topics

Hi I want perform the comunication (ethernet) between ML 1400 (IP: 192.168.1.11)and Red Lion HMI G304k200 (IP: 192.168.1.20). I wrote the...
Replies
6
Views
5,251
Hi What is the best solution to have a comunication between a PC (XP OS) with a HMI CX Supervisor and a PLC OMRON CQM1H? The distance between...
Replies
0
Views
2,067
hi i just know the number of comunication wincc with cpu314 siemens because i have a probleme resource failed to comunicate 5 pg to cpu 314-1ag13-0ab0
Replies
0
Views
1,334
I have an old plc in the system I have, moxa nport was used to communicate with scada, I want to replace the plc with cj2m cpu33 and eliminate...
Replies
1
Views
84
Hello all. I have a future project planned with a leibinger jet3up inkjet printer that I will have to send the print details to the printer via...
Replies
4
Views
1,252
Back
Top Bottom