Connect ProTool Runtime to WinLC
Garcia
Apr 2006
Pittem
37
Hello,
I have the following configuration:
Siemens PanelPC 577
CP5611
WinLC V4.0
Protool Runtime
ET200S
So far all the installation/configuration has worked out fine. The CP and WinLC are installed on the panel PC. The project is created on my PG. The remote island is connected with the panel PC, the hardware config is downloaded and all the red lights (on the island and the WinLC) are gone. I have added a protool application in the station configurator on the panel PC and in the project on my PG. I have compilled the the Protool appilication and transferred the .FWD file with a memory stick to the panel PC. The protool application runs on the panel PC but is unable to make a connection with the WinLC. I have tried both protocols (S7 300-400 and WinAC).
Are there "special siemens tricks" that need to be done in Step7, the station configurator on the panel PC or WinLC?
I use Step 7 pro V5.4 SP1 and ProtoolPro V6.0 SP2
Thanks for reading, and hoping for an answer,
Bert
Maybe I can help
I have same type of setup but with WinCC Flexible WinAC RTX and CP5613.
The connection should be S7 300/400 so that should be fine. You said you put the ProTool project into Station manager. I have Flex setup in slot 3. You need to make sure you are using the same slot in HW config. I would check the station first.
Hi Charles,
Thnx for your reply. I have check my station configuration and HW configuration again and everything seems to be in order. The only difference i find, is that you use WinCC and I use Protool. Below a picture with the error message i get in ProTool RT.
This is my config;
The only thing I see is that you have WinLC configured in the station and PC577 in the HW config. You may have the correct part number in HW config but I can't see all of it. Thats the only thing that I change. You could go to Siemens tech support site. I have seen a FAQ about setting up Flex with WinLC. It may have something in it that would help.
Please post what you find as the problem.
Charles,
My Version of WinLC is de basic version, you have the RTX version. Hence the other order number. I also tried to change the names etc. of the devices. Nothing seems to solve the problem. I also found help on the tech support site, right here: http://support.automation.siemens.com/WW/view/en/17602788
I have done exactly what is written in the help file, doesn't work.
Now I have send my project to our Siemens supplier here in Belgium, to ask them what I do wrong. Hopefully they will find the problem.
Thanks for help.
Bert
i finished a new project by protool v.6 sp3 on win xp , i have S5 TTY Programming Cable when i connect to op 15 display transfer ready but when...
1,286
Hi, i've got protool project for Tp 270 that signalises fires on the plan for the emergency fire unit. It works well but... When the MPI plug is...
5,156
Greetings, I had an issue with a RIO rack 2 and IFM I/O Link dropping on my network. I would loose connection for a second or 2 then they would...
84
Hi friends, i need a help to know the procedure and steps to connect Lenze i700 to PC for parameterize. i tried with lenze easy-starter using LAN...
46
Hi, We have been facing a issue with SCADAPack 474. Configuration is like below. RTU 474 + 6103 PS + 5606 IO Mix Module + 5414 DI Module Only...
73