Connecting analog output module to 24V AC (0-10V) instrument
flyers
Sep 2006
Amk
295
Hi guys,
I've a field instrument (actuator) using 24V AC, 0-10V.
The terminal connection as below:
Terminal 1 = 24VAC
Terminal 2 = 24VAC Com
Terminal 3 = Com (jumper with terminal 2)
Terminal 4 = 0 to 10V
The Analog module I'm using is Siemens S7-300, as per below link.
6ES7331-1KF02-0AB0 SM331, 8AI, 13BIT
http://support.automation.siemens.c...tandard&viewreg=WW&objid=15324473&treeLang=en
Can the Siemens module, suitable for this actuator?
Thanks guys.
No, you need an AO for an actuator.
Also the suggested I/O is rated for ATEX and hazardous areas. Is it really necessary? Costs$
Hi guys,
Terminal 1 = 24VAC
Thanks guys.
It would help if you could post make and model of actuator (or data sheet).
Karsten is correct. If we are to assume you will control the actuator with this 0-10VDC - and as moggie says, we could really use the actuator data sheet to know that for sure - no, you need an Analog Output card. On the other hand, if we assume you are monitoring a 0-10VDC feedback from the actuator, then yes, the card you have selected is suitable.
Steve
Can anyone give me diagram when connecting a conrol valve (with two terminals - 4-20mA) to PLC Analog Output module? Thank you..
5,288
Hi All I want to mov the cuttent count of a HighSpeed to a register so that I can scale an analog output. I use a mitsu FX1N with 2 A-out...
5,309
Just asking for clarification here, but from my research all I need is a 500 ohm resistor across the AI and the common? Heres my schematic. I...
2,586
Hello everybody. for an asignment we are using a s7 1200 siemens starterkit to connect sensores to create a program. we were hoping to save some...
6,498
Hi everyone Hope I can get some help in this: I had a quick read about the EASY822-DC-TC datasheet and still don't get how to connect an analog...
2,143