Hello guys

Iam New in S7-300 if you please help me in that

Does any body tell me the connection link between CPU and SM?
and How to replace a Signal Module(Analogue or digital?
 
Hello Moustafa.

The backplane of the S7-300 consist of U-shaped connectors that link the next SM module with the previous SM module. The same type connector links the 1st SM module with the CPU. The U-shaped connectors sits at the base of the SM modules.
To replace an SM module, you have to remove power from the S7-300 rack, remove the front terminal block, loosen the screw at the bottom of the module, lift out the old module by tilting it upwards - then do the same steps in reverse order with the new module.
The U-shaped connector will be retained by the modules that stay in the rack, so you do not have to add the U-shaped connector to the replacement SM module.
 

Similar Topics

I replaced a PanelView 600 with a PanelView Plus 1000, graphics was successfully transferred over. When connecting the D-485 Link Coupler via the...
Replies
7
Views
3,612
Did anybody try to set OPC connection via dialup phone line? If it is possible, what troubles can occurs with DCOM configuration? Thanx a lot.
Replies
1
Views
2,758
Hi dear . I have a system with cj1m cpu11 etn. previously NT 5z HMI was connected with plc. recently my old HMI got damaged. I want to replace it...
Replies
12
Views
256
Hello gentlemen, Im working on a small project on TIA Portal, about establishing a Modbus TCP connection between my ET200SP plc and a socomec...
Replies
12
Views
313
Hi all, My ethernet port on my laptop recently broke and I was hoping to just use a usb-c dongle in the mean time to go live on my PLC until I...
Replies
14
Views
454
Back
Top Bottom