I'm working on a vibration test machine that uses a VFD to control a set of counter weights to create specific displacement test. What I need to do is control the freq and rate of the sweeps. A typical sweep is 8-60hz at 1hz/min. Any good ways to do this?
 
I would chose a servo motor instead of a VFD.

A PLC is not fast enough and I don't know of any general motion controllers other that ours that have built in sine waves with linear and logarithmic sweeps and amplitudes can be changed on-the-fly.

In the test arena we are usually competing with MTS ( Minnesota Test Systems ). The advantage MTS has is that they will sell you a complete system and they know what they are doing. Our solution is usually our RMC75 controller, Lab View, and an integrator that can put all of that together. Our solution is cheaper and more flexible the integrator must be fairly knowledgeable. I am usually in the back ground verifying the design.

If you choose some other solution make sure they have a successful track record because most people that try this on their own screw it up.

Sinusoidal test systems are more difficult that they appear. Most designers grossly under estimate how much power is required or over estimate what they can do with the power they have.

The amplitude and mass or inertia was not specified but I will give an example of what people under estimate most often.

The power at the load is proportional to the frequency cubed. That is a 60 Hz oscillation will require 8 times more power than a 30 Hz oscillation unless the amplitude of the 60 Hz oscillation is reduced by a factor of 8. This calculation doesn't take into account the power lost getting it to the load.

It is good to have the system modeled before picking out equipment.
 
Amen and Amen to Peter's comments. We've been asked lately to simulate internal combustion engine torque pulsations in test cells with an electric motor.

We have only been successful at relatively low frequencies and then with huge power and braking levels.

Definitely go with someone experienced at this. It's a huge challenge!
 
Look how an old steam engine works.
the vfd is fine for the motor generating the vibration.
the amplitude is easier with a mechanisme.

it is also possible with a loudspeaker and a wavecontroller (expensive but controlable.
 
I would just use comms from a PC to the drive, then just increase the frequency by 1Hz every minute. At the low speeds especially, I think you may want to do this closed loop if you need tight speed control.
 

Similar Topics

Hi Everyone, I am new to siemens servo drives, needs some helps and wondering if you can help me. The machine has Siemens S120 Servo Drvie and...
Replies
2
Views
1,656
Hello, please its possible to control flow rate using frequency mode of a flow meter ? if yes, how is it done for a PLC like Micrologix ? i...
Replies
10
Views
2,225
Hi, please I wish to develop project like this: I wish to control my flow transmitter using PLC. For example If i wish to pump 1000, 2750 0r 3800...
Replies
6
Views
2,091
Hi everyone. I'm working at water treatment plant. I have some filter sand, every filter sand have a vavle analog use cotrol flow, a transimiter...
Replies
8
Views
2,404
Hi, I am new to PID control, wondering if anyone can help me with this. We have a flow meter goes into VHSC point io card as input, analog output...
Replies
2
Views
2,083
Back
Top Bottom