usmcgrover
Member
Anyone out there doing this?
I have a PLC5 system in place that uses 1771 I/O. I'd like to replace the PLC5 with a C/L processor and set up the 1771 I/O as remote I/O using a 1756-DHRIO and a 1771-ASB.
Right now, I have the C/L and 1771 rack set up at my desk. The ASB module I have is old (series B) and it won't talk to the DHRIO, so I'm wondering if there is an issue between the DHRIO and a series B ASB. I hope not, as the system I want to convert has about 8 remote racks and all of them have series B ASB modules in them.
I'd appreciate any shared experience with a project like this.
Jeff
I have a PLC5 system in place that uses 1771 I/O. I'd like to replace the PLC5 with a C/L processor and set up the 1771 I/O as remote I/O using a 1756-DHRIO and a 1771-ASB.
Right now, I have the C/L and 1771 rack set up at my desk. The ASB module I have is old (series B) and it won't talk to the DHRIO, so I'm wondering if there is an issue between the DHRIO and a series B ASB. I hope not, as the system I want to convert has about 8 remote racks and all of them have series B ASB modules in them.