Controllogix LED's?
RPax
Feb 2004
125
Hi, just a quick question on a ControlLogix processor as not over familiar with these. Was wondering if the OK LED on the processor module is contantly red does this mean it's "Knackered". Says in the manual to contact your local rockwell representive. Always worry when I hear this!.
Only using the processor to gather analogue data and sent to server via the ethernet but at moment this doesn't seem to be happening.
Mind you the run light is still on and have an ethernet module that still seems to be communicating from visual inspection. When I try to log on via the RS232 it can't communicate with Laptop. That said, have a consistent red light on this RS232 LED also. Appreciate any help. Thanks - Rpax
There are six LEDs on the front of a ControlLogix controller. If I read your post correctly they are showing as follows:
RUN Solid Green
I/O Off
FORCE Off
RS232 Solid Red
BAT OFF
OK Solid Red
Generally when you totally lose the program in a controller you have a solid red LED on the OK LED and nothing on the others; a solid green RUN LED and solid red RS232 sounds like a nonstandard fault.
Since the controller's not running, it can't hurt to pull it out of the rack to cycle power. I don't think it's completely knackered, just faulted.
Yeah thats the current light arrangement, will try re-cycling the power, thanks for the reply
Yeah, bottom line once you recycle the power you'll lose the Program but processor is still good. Thanks for help Ken
I bought a used L55M23 processor on Ebay and turns out that it doesn't work. RSLinx can't find it whether by RS232 or Ethernet adapter. With this...
3,504
Hi there, Can I only force outputs to stay Energized/On or De-energized/Off or does this work within a ladder logic program on temporary coils too...
1,792
There is a chilled water cooling loop in our process cooling a roller. It has been about impossible to tune. this is in a tertiary loop. From the...
3,239
ControlLogix 1756-L71 version 20.55. I want to poll this controller from two separate GE iFIX 5.5 SCADAs using the IGS 7.58 driver. Each SCADA...
1,369
I need help with programming a 1756-L61 v16.21. I want to track if the main power to the PLC was cycled, and IF possible the date and time for...
2,550