Controllogix PID overshooting CV High Limit
May 2017
Regina
Hello,
I have a PID that I am using for an oxygen valve that regulates the pressure. Often when the header pressure is too low, the output will reach 123%. My CV High Limit is set to 100%. Why would this exceed the limit?
1756-L73 Processor V23.12
2018-10-29 PID Tuning.JPG 2018-10-29 PID Configuration.JPG 2018-10-29 PID Scaling.JPG
Based on those screen shots, it appears that your .CV is scaled 0 to 1000, corresponding to 0 to 100% output. So a CV value of 123 will be 12.3% output of the loop.
Yes, but the Output % is reaching 123%.
According to the Allen-Bradley documentation (see attached), output limiting is the last thing to happen before conversion to CV. I don't have a good explanation unless external logic is writing to .OUT and the PID is not being scanned.
I think I've figured out my issue. I was retrieving the Setpoint from the Rosemount valve via an OF8H. For whatever reason the extra 23% is only the feedback from the valve. Ive since changed it to the PID output. Thanks for the help.
Morning all, Could anyone shed some light on whats happening with my PID Loop? On our plant we have a 'fast ramp' on the PID Instruction done...
7,614
Hello all, I have a pump that has operational limits 15-100% Speed (9-60Hz). 1. On the PID instruction would you limit (.MINO=15% and...
21
5,168
Why is my PID .PV (Process Variable) getting continually overwritten with some strange value every time the rung my PID Instruction is on goes...
2,138
Hi there, I have a PID which I limit at MINO = 25% and MAXO = 100%. When the PID runs for the first time it takes time to start reacting at 25+%...
3,069
Hey fellas, I'm in the midst of doing my first translation from 5 to 5000 that also includes PID instructions. I'm just looking for any helpful...
5,519