After a little help. We have ControlNet set up in redundancy - how do i show which channel is active in the PLC code? Can see all the info on the module pop up when removing cabels etc (channel A active, channel B standby), but can't find where to get that info to relay to the PanelView. Also can't seem to get the indication on what's happening when one of the cables is pulled out (it's actually all working OK, just need to display what's going on).
Any help appreciated.
Thanks,
Chrispie
You need to use GSV's. Within the instruction you can select to get the info from redundancy module, processor or specific modules in your rack (controlnet card). The help on GSV's (press F1 while the GSV instruction is highlighted) tells you which parameters you can get.
The specific LED state and Channel A/Channel B connection status requires a CIP Generic Message.
This is detailed in RA Knowledgebase Answer ID #18423.
Other nifty stuff you can do with CIP Generic Messages is described several other Technotes. A table of contents of these technotes is provided as RA Knowledgebase Answer ID # 24538, CIP Messaging Reference.
I’ve mentioned bit of this before, http://www.plctalk.net/qanda/showthread.php?t=68356 Its a bit long Last year I inherited a system...
4,226
Hi all, I have, Rack1 : L62,EN2T,CN2R,RM Rack2 : L62,EN2T,CN2R,RM (All are upgraded as per 19.5 Redundancy Bundle) With this...
2,869
Hello, I have a running ControlLogix Enhanced redundancy system: The first chassis has in Slot 0 the Controller, in Slot 1 the Redundancy...
1,688
Hiya all, Previously setup a standard ControlLogix redundant system and all works well. (2*7 slot rack, 1*L63 CPU, 1*Ethernet EN2T, 1*Controlnet...
2,246
Hi Everybody, I have a question regarding ControlNet in ControlLogix redundant configuration. I have two ControlLogix PLCs working in a redundant...
5,769