Convert Long to Float with Micrologix 1400
josehr
Jun 2011
CA
Hi all,
I am communicating with a modbus device which sends data in 32 bits format.
The MSW represent the integer part of the value and the LSW represent the fractional part as an UINT16.
How can I transform that long into a float number with the right result?
Scale X .Y indicates a binary fraction where…
X specifies the number of integer bits
Y specifies the number of fractional bits
value = integer part + (fractional part / 2^Y)
Example:
Scale = 16.16 revs X = 16, Y = 16
Raw Value = 131109
131109 decimal = 10 00000000 00100101 B
integer part = 10 B = 2 decimal
fractional part = 00000000 00100101 B = 37 decimal
Final value = 2 + 37/2^16 = 2+16/32 = 2.000564
Jose
Welcome to the forum.
Since MODBUS is 16 bit by default I suggest you start by placing the information in two consecutive N words first. You can do this with a CPW #L9:0 #N7:0 1
If N7:0 contains the MSW and N7:1 contains the LSW then it gets pretty easy to compute.
First step is to determine how many digits are in N7:1. The LOG function can do this EXCEPT it is going to have problems with 0 values and rounding when casting the result to an integer, so instead of trying to trap and fix the exceptions I recommend using five compares.
LES N7:1 10 MOV .1 F8:0
LIM 10 N7:1 99 MOV .01 F8:0
LIM 100 N7:1 999 MOV .001 F8:0
LIM 1000 N7:1 9999 MOV .00001 F8:0
GEQ N7:1 10000 MOV .000001 F8:0
(The final compare may not be necessary, refer to your device documentation regarding its range)
Now a CPT statement can assemble your float.
CPT F8:1 N7:0 + (N7:1 * F8:0)
This is assuming that the data format is what you have described and not an IEEE-754 float format. If its the latter then the solution is easy, a CPW instruction with a floating point destination will do the trick.
With the fractional part in N7:1 (after Alaric's CPW) preserve a copy of N7:1/15 (true or false) then set N7:15 to 0.
Then the fractional part is N7:1/65536.0 (obviously the '.0' is to force it to a float calculation.)
Finally, if N7:1/15 WAS SET then add .5 to the fractional result.
The resetting of /15 is done because otherwise, if it was set, the value of N7:1 passed to the calculation would be negative.
Thanks a lot for your help.
I tried Bernie approach and it is working perfect!!
I need to do the same in the opposite direction now to write the setpoints to the device but I got the idea.
Regards
Jose
Hi all, I'm communicating with a modbus device which sends data in 32 bits data. You can see the structure in this example: N7:4...
4,608
I have an Allen Bradley MicroLogix 1400. I am trying to display a value onto an HMI, however my HMI will not accept a Long (i.e. L10:2) as an...
10,625
Using Logix 500 with a AB Micrologix 1100, I need to convert a 5 character string to a long. example 99999(string) to 99999 (long). The function...
3,191
Hi! What is the way to convert the code from the Codesys code to the Tia Portal? Regards, WK
99
Hello all, I'm currently working on a servo motor linear positioning system (ball screw). I'm all set up regarding communication between my HMI...
133