Convert PLC5 integers to ASCII in RSVIEW32
mulderm
Jun 2003
Netherlands
298
Hello,
Another problem for me using RSView32 (I am new for this).
I will bring the Integer values in the PLC5 converted to a ascii value in a display in RSView32.
Example:
I have in a PLC5 3 words: N11:0 = 14385 (ASCII=81)
N11:1 = 13881 (ASCII=69) and N11:2 = 13113 (ASCII=39).
So I want the value 816939 seeing in a display in RSView32.
How must I do this?
Greetings,
mulderm
you have two modes:
1.- If you use RSLINX DH+ (direct connection), you must choose the first word (N11:0) and its length: 6
2.- If you use RSLINX OPC, you´ll need string.i.e: ST25:0= 816939
Anyway the tag created was string and you must use a display string in Rsview.
regards