Hi guys,
I am using a Beckhoff EL1512 counter card to count pulses from a speed sensor. This sends a 24VDC pulse when close to a gear tooth.
The counter card required 15-30vdc for a logical '1' and -3 to 5vdc for a logical '0'. Typical input current 5mA.
The speed sensor is an open collector type, 3 wired (0vdc, 24vdc and output pulse) the output pulse is 21VDC with no load, as soon as connected to the couner card and a contact is made, the voltage drops to 7V, the pulse input lamp is lit but dimly on the counter card but the count is not incremented as the voltage is under 15VDC.
With my meter in series, the speed sensor is limiting to 2mA that is why there is a voltage drop.
If I use a wire and short directly between the pulse input (clock) and 24VDC, the pulse input lamp is much brighter and the count is incremented.
This is the spec on the speed sensor:-
- Open Collector outputs with
10Kohm pull-up, lmax = -20mA
The outputs are short circuit
proof and protected against
reverse polarity
My question is, is 2mA very low for a open collector speed sensor (I know a transistor is switching but seems very low)
Also the spec on the speed sensor says Imax = -20mA. why is it limiting at 2mA then?
I have tried the sensor just with a power supply (0vdc and 24vdc connected to power speed sensor) and as the output is short circut proof, by placing a multimeter on current in series with the output and the other side to 0VDC, when contact is made, the maximum current is still only limited to 2mA.
The speed sensor supplier have said they have never had any problems but 2mA output limit sounds very low.
Any help appreciated
Matt
reverse polarity
Matt