CPU did n't give the output,Istack message enclosed
kareemmm
Aug 2007
KSA
Now we are facing a problem that our S5-115U is not working proper Last time we have a power failure in our plant and when restart the plant I saw in the plc message that battery low. I replaced the battery and energize plc. But it didn't give the out put. So I reload the program again but I can't cold start the plc, Then I use the trouble shoot using our SIEMENS FIELD PROGRAMMER and the following are the ISTACK messages I request pls. give the solution and what may the problem
SIEMENS SIMATIC S5 PS 3A 115U CPU 942B DIGITAL INPUT
32 X DC 24V 3CARDS
DIGITAL OUTPUT
32 X DC 24V 4CARDS
img]http://www.plctalk.net/qanda/uploads/Image1452.jpg[/img]
img]http://www.plctalk.net/qanda/uploads/Image1453.jpg[/img]
I Have a question to you, what is the status of your PLC upon replacing the battery? What is the status of the LED in the CPU?
Give us some detail regarding the problem! o_O
Regards
Sherwin
kareemmm said:
Yes and I try to RUN PLC thru PG but the message is cold sutart is not possible
try to put the switch in the unit( PLC ) to stop mode then return the switch to run mode. The green light should lit as run.
have u done overall reset of the CPU?
DO the overall reset and then reload the program...
The procedure is as follows:
Switch on the power supply module
Set the CPU mode selector to STOP (ST)
Set the switch for "Default/Overall Reset" to the "OR" position and hold it in this position.
While you hold down the switch for "Default/Overall Reset" in the "OR" position:
Switch the CPU mode selector twice from "ST" to "RN".
The STOP LED will momentarily go off.
Release the switch for "Default/Overall Reset".
The switch automatically springs back to the "RE" position.
The internal program memory and any RAM submodule (plugged into the CPU 941/CPU 942) are now "overall reset". After Overall Reset, the CPU automatically tests your internal program memory; in the event of a fault, the STOP LED flickers.
Set the CPU mode selector to STOP (ST)​
Set the switch for "Default/Overall Reset" to the "OR" position and hold it in this position.​
While you hold down the switch for "Default/Overall Reset" in the "OR" position:​
Switch the CPU mode selector twice from "ST" to "RN".​
The STOP LED will momentarily go off.​
Release the switch for "Default/Overall Reset".​
The switch automatically springs back to the "RE" position.​
The internal program memory and any RAM submodule (plugged into the CPU 941/CPU 942) are now "overall reset". After Overall Reset, the CPU automatically tests your internal program memory; in the event of a fault, the STOP LED flickers.​
Take note of this! Check first if the program is still in the CPU, don`t overall reset the PLC if you don`t have a back-up copy of the program. Check the program and compare it to your back-up copy. Some time overall reset is not the best solution to your problem, just a piece of advice.:)
Regards
Sherwin
I have seen a similar problem. I had a card go bad on a S5 and went to stop. It happened on power up. I pulled each card one by one and tried ro go to run. When I came across the bad card, it went to run. I replaced the card and everything was fine.
kareemmm said:
Yes I done
and now it works proper
Many many thanks to Mr.Rohan,Sherwin,Maj.Toxido,Kev 77 and all the forum members
With regards
Kareem
[email protected]
+966502849897
Awww, I feel hard done by now, I just noticed this thread, you had another where you did not put the pictures in, the only reply from me and that was to do an overall reset... :whistle:
Now we are facing a problem that our S5-115U is not working proper Last time we have a power failure in our plant and when restart the plant I saw...
1,962
Hello everyone! I need to connect to a DL205-1 CPU and, as far as I know, I need to use DirectSOFT 6 software for the connection. Is anyone...
66
hello s7-400h and wincc are connected to each other via Ethernet. I need help on how to do time synchronization
54
I'm struggling to get an FR-E800SCE to work on CC-Link IE TSN. I'm sure the issue is with the drive, when I plug in the network cable I get no...
105
Hi , Where i can find Mitsubishi PLC Card end of line & replacement model details. i am looking for Q02CPU replacement model. Please advice. thanks
126