CU240E-2 DI0 does not work
Piiok
Dec 2022
Poland
HI,
I'm using siemens G120 drive with CU240E-2. Previously was working DI0, DI2 and DI 4 in configuration with COM 1.
Unfortunately right now DI0 doesn't work, when I'm connected via TIA Portal 16, Sinamics Startdrive advanced. DI 2 and DI 4 still working.
This drive works on the production line and I don't know if sb change in params.
Does exist some parameters regarding digital inputs to activate/deactivate it ?
What does the input look like in Startdrive?
Is the "led" for DI0 on?
Are you getting 24vdc to the input? put your voltmeter between terminals 5 and 28
How is the input programmed?
Hi thank you for your reply JRW.
answer:
my original conf was like in attached photo. Right now I changed p840[0] from DI0 to DI4 because DI0 does not change its status to high even if I put 24 voltage.
answer:
No. I put 24 V on it, and no high status. But DI2 and DI4 work correctly, 24V to input and in software I get high status for them.
answer:
Yes I measured it. But I don't use 28 GND. I'm using COM 1 for low potential 0V.
answer:
you can see in attached files.
My another question is, how to wired correctly to use another inputs DI1,DI3,DI5 ?
Hi JRW,
Thank you for your reply. Sorry for late answer but I've already today had access to machine.
DI0 looks is doesn't work at all.
Anyway, I went by your advice and configured another input DI1 (instead DI0) using COM 2. COM 1 and COM 2 have right now the same 0 potential.
I'll observe how does it work and if there is no other malfunctions.
If could you have some tips how to protect digital inputs against overvoltage I would be greatfull. And also what kind of supplier to use.
Right now I have separated galvanically, supply of digital inputs with digital outputs of beckhoff card by relays.
Thank you for all very helpfull information !
Hello again,
I would like to refresh subject.
Recently once again one input DI4 with signal p840 ON/OFF was damaged (I cannot see any change of status in software although it is energized 24V).
This happend second time, for a first time damaged was DI0, right now DI4.
Inputs are energized from DELTA 24V supplier. Electric voltage is ,controlled via relays which are sterring by PLC.
What could be the reason that two inputs were damaged ?
I think that maybe you get voltage spikes on the common 0V. And possibly it is just a coincidence that it is the VFD inputs that gets damaged before anything else.
Check if you have large contactors, solenoids or any other inductive loads, that they are equipped with surge suppressors. If the inductive loads are on a different voltage system but share the same ground, it can affect also the 24V system.
Check that your 0V is grounded.
Check that your earth is good enough.
hi am a beginner in controlling the G120 VFD can you give an easy-to-understand source about controlling G120 vfd with (CU240e-2-pn) unit using...
759
Is it possible to update the firmware of the device in the title through TIA Portal?
2,096
Hello, I need to program a CU240E v4.4 with a PM240 power module and a BOP-2. The client wants following DI mapping. DI 0: Start remote...
1,578
Hi I have a ifix 5.5 application where the operator opens a valve by clicking on a screen object. I can trace from object to data base that it is...
46
Hi, i am using DVP-14SS2 PLC, after program written to plc, when power is reset, plc doesn't run. always need to connect to pc for the run mode.
39