As I said when I started, 20mA input gives 4200. 0mA input gives -17. Even if the source was not calibrated the in series Fluke meter read the same mA value. The value should have been much closer.1) I'm not sure it's the AI that might be out of calibration. What was the source that was used?
2) I'm not very clear how a 12 bit board whose A/D does 4096 counts is supposed to cover a 0-5,000 count span.
Through internal multiplication. Same as you would do in a rung of logic. Same way it works for lesser values.