Cycle Count retention during power loss
busarider29
Aug 2013
Midland, MI
400
This is my first post but I have a couple questions. First, the PLC that I'm using is a SLC 5/05 with RSLogix 500 V.9.00. What is the best and most efficient way to count cycles when dealing with cycle counts in the 500K range? I just want to know if there is an easier and more "cleaner" way to do it than what I'm doing. Also, during a power loss (we get frequent facility power losses), can I retain that cycle count in the PLC, so that we can start up again and begin cycle counting where we left off before the power loss?
All and any help or advice is much appreciated.
- Don
Welcome to the forum.
Use a floating point number address, a one shot, and an add instruction.
Cycle_Start B3:??
-----] [--------[OSR]-----------+-ADD----------+
|Source A: F8:0|
|Source B: 1.0|
|Dest F8:0|
A floating point number will be good for counting to 16,777,216 cycles, then it starts to loose resolution in the 1's column.
All addresses in a SLC5/05 are retentive, they do not change unless operated on by an instruction, so unless some other instruction changes the count value then it will be retentive though a power bump.
The value is not retentive through a PLC program download. If you download the program then the last saved count will be downloaded as well. You will need to establish some kind of protocol for making sure the offline value is updated to the correct value prior to a download. One way is to keep the key switch in the run position and placing a tag on the key reminding you to upload the correct cycle count first.
For critical cycle counts I either use an external counter or if an HMI is attached I log the cycle count to a database.
Hi i have project on micrologix 1400 to display cycle time count on HMI. I am beginner. in project i have six input once all input get high it...
833
As Johnny Cash would have said "I've been everywhere Man" Surfed the net for three hours, finally gave in and asked Rockwell. They said they...
2,150
Hello all, I've got a problem that I need to get addressed this is a new project for the company and I've gotten myself a bit lost on this. I've...
3,589
Hello all, I'm new to the plc world here. Most of my experience is from CNC machines and some Motoman NX100 programming. I am currently working on...
3,010
Hello PLC friends. I've been going through a saga of diagnosing and fixing an old PLC setup that I inherited. I am learning as I go. Initial...
382