I don't see why DC would be any different from AC. Just consult the NEC ampacity chart for AWG wire sizes and go by that. If the wire lengths are long, you may want to oversize to reduce line voltage drop.
NEVER skimp on wire size for motors. Bigger (within reason) is always better.
FIRST read motor nameplate and get all the amperages.
Then decide if those are applicable to a single line feeding motor.
IF you are real lucky you will have a manua for the motor and it may tell you with a chart what size conductor to use for what distance.
After that almost any electrical book or NEC or other code agency will have calcs.
To calc volt drop find wire resistance multiply by two and by length ot motor and then multiply by amps. This should give you IR drop which should be around 3% or less.
IF in a real hot work environment you will ahve to derate for ambient temperature.
IF your question is for 3 phase feeding a solid state controller you may have to derate for number of current carry conductors in pipe or cable (if more than 3)
Dan Bentler
Hello everone I need to make 33m cable for the TLP motor. What choice should I make about this? We will make the cable ourselves. What kind of...
1,024
We are looking into installing a well water pump (480vac, 25hp, 40FLA) with a PowerFlex 755 VFD. The challenge is that the well is located about...
4,716
Hi, I have a stepper motor with integrated driver, the driver needs a pulse input signal and direction input (see...
2,205
Hello I normally run VFD cable from the drive directly to the motor un-interrupted, with a good shield connection at the drive end, and an EMC...
3,270
Anybody ever see this before? I've got a 60HP motor on a drive that has been drawing a little higher than normal currents, about 125%, something...
3,634