I have a new install with a slc 5/03 and devicenet scanner. The network only has 1 node, a numatics valve bank. Is a 1770-KFD or 1784-PCD the only way to bridge onto the network or is there another way that might be easier to configure only 1 node. Thanks
 
1747sdnpt

Configure RSLinx Classic to connect to the SLC-5/03 over DH485 or DF1 Full Duplex, then configure a "Passthrough" DeviceNet driver, specifically the 1747SDNPT driver.

The RSLinx Classic Help file and the 1747-SDN installation manual help with the M0/M1 file configuration and other steps necessary to get the Passthrough driver working correctly.

The "Passthrough" drivers for PLC and SLC scanners are a lot slower than a direct (-KFD or -PCD) or ControlLogix bridge interface, but they don't cost extra and are fine for a small system.
 
Ken Roach said:
Configure RSLinx Classic to connect to the SLC-5/03 over DH485 or DF1 Full Duplex, then configure a "Passthrough" DeviceNet driver, specifically the 1747SDNPT driver.

The RSLinx Classic Help file and the 1747-SDN installation manual help with the M0/M1 file configuration and other steps necessary to get the Passthrough driver working correctly.

The "Passthrough" drivers for PLC and SLC scanners are a lot slower than a direct (-KFD or -PCD) or ControlLogix bridge interface, but they don't cost extra and are fine for a small system.

Passthrough only works with above x.xx fw in the scanner (cant remember the fw number at present) so if its a new scanner it will probably be fine, if its an old scanner then check as it may not work.

edit: found it 4.015 or later

passthrough.jpg
 
Last edited:
Knowbase Answer ID # 6944 has the details on the configuration of the 1747-SDNPT driver in RSLinx Classic. This information is also in the Online Help for RSLinx.

The firmware revisions and M0/M1 file size settings are:
361 elements for Rev 4.015, 4.026 and 5.01
395 elements for Rev 6.02 or higher


I know of a bug in version 8.02 of the 1747-SDN firmware that will fault the CPU if there is nothing connected to the DeviceNet and you perform a browse. Solution: connect power and slave devices to the DeviceNet you are trying to access.
 

Similar Topics

Hello, a while back ago i posted a question about device net communications between an allen bradley PLC5 and a micro motion flow meter. I never...
Replies
2
Views
1,508
Hello, I'm trying to setup a devicenet network using an AB 1769-SDN devicenet card with an Omron CJ1W-DRM21 device net card. The AB will be the...
Replies
1
Views
2,010
I'm trying to use a micrologix 1500 with a 1769-SDN devicenet card to communicate to an Omron CP1H using the Omron CJ1W-DRM21 card. Does anyone...
Replies
6
Views
2,175
I need to know if anyone has used an AB ControlLogix with a Devicenet Scanner to control the I/O in an Omron C200H? From what i can find I think...
Replies
1
Views
3,109
Hi. We've been asked to do an upgrade on plant, consisting on a PLC upgrade. This involves replacing a 1747-SDN module to a 1769-SDN, in a network...
Replies
0
Views
65
Back
Top Bottom