Devicenet Communications
rockyh
Oct 2010
Oregon
I'm trying to use a micrologix 1500 with a 1769-SDN devicenet card to communicate to an Omron CP1H using the Omron CJ1W-DRM21 card. Does anyone have any info on setting this up.
Both of those devices have the ability to be configured both as a Master or as a Slave.
Which one do you plan on making the Master ?
Do you have the Omron configuration software, or RSNetworx for DeviceNet, or both ?
Then it ought to be pretty simple.
You'll need a slave EDS file for the Omron device, and a physical way to connect to the DeviceNet network. The MicroLogix 1500 doesn't support "passthrough" from the controller to the network.
The 1770-KFD and the 1784-U2DN are the most common methods for connecting to a DeviceNet. Bridging through a ControlLogix 1756-DNB or through a CompactLogix 1769-SDN are also common.
In RSNetworx for DeviceNet you add the Omron device to the Scanlist of the 1769-SDN, use the AutoMap function or manually configure where that data is going to be in the Input and Output files of the scanner, and download that scanlist configuration to the 1769-SDN.
I have the eds file for the Omron controller and have started the project in RSnetworx already, it's just where does the I/O mapping go as far as the Omron Devicenet card is concerned. Am I going to have to configure that as well.
Hello, a while back ago i posted a question about device net communications between an allen bradley PLC5 and a micro motion flow meter. I never...
1,507
Hello, I'm trying to setup a devicenet network using an AB 1769-SDN devicenet card with an Omron CJ1W-DRM21 device net card. The AB will be the...
2,010
I need to know if anyone has used an AB ControlLogix with a Devicenet Scanner to control the I/O in an Omron C200H? From what i can find I think...
3,109
I have a new install with a slc 5/03 and devicenet scanner. The network only has 1 node, a numatics valve bank. Is a 1770-KFD or 1784-PCD the only...
3,497
Hi. We've been asked to do an upgrade on plant, consisting on a PLC upgrade. This involves replacing a 1747-SDN module to a 1769-SDN, in a network...
64