DH 485 Comm (SLC 5/05-1761 AIC-PV 550-PC)
Microbictomb
Mar 2015
Michigan
56
I saw another thread similar to my issue but I have different equipment and didn't want to jump on that one so here is mine:
PanelView 600 2711-B6C2 Rev. C Frn. 3.30
SLC 5/05 1747-L551 Ser. B Rev. 4
1761-NET-AIC Ser. B
Windows 7 Pro 32 bit
RSLinx Classic Pro 2.59.02 CPR 9 SR 5
My PC is connected to the AIC module using 1761-CBL-AP00 Ser C
The PV 550 is connected to the AIC using 1761-CBL-AS03 Ser A
And the SLC 5/05 is connected to the AIC using 1747-CP3
External power switch is on with 24VDC external applied to AIC and Auto for baud (tried 19200 as well)
Node address/Baud setting in PV is Node 2, 19200.
In RSLinx I selected RS-232 DF1 devices, Auto configure. SLCCH0/Micro/PanelView is configured and communication works with the processor through the AIC.
Browsing in RSLinx, Node 0(PC) and Node 1(SLC) are found but not the PV. Under Config-Communication in the PV the comm led is flashing and "No active nodes found on network" is displayed.
Now I read somewhere that you have to configure channel 0 in the SLC to DH 485 so I tried that. I lost all communications with the processor completely after I downloaded the change and had to reset it to factory defaults and re-download my program(not a big deal, small ladder and PLC is for testing only). I know I'm missing something here but I just can't see what to do next and would greatly appreciate any assistance.
The ultimate goal is to get communication established over DH 485 in order to work on a PanelView 550 2711-T5A2L1 Ser. A Rev. E Frn. 4.10 which is not functioning properly and I want to see if I can at least get comm's established to possibly download a new PVA application and bypass/remove the current program/password. Since I am unable to get to the config. screen I am using the PV 600 in lieu.
If you want your SLC's serial port to communicate with a PV that supports DH485 protocol then the SLC's serial port must be configured for DH485.
If you want your PC to also communicate with a device configured for DH485 then RSLinx is going to have to use a DH485 driver. If the PC has a real serial port then the 1747-PIC/AIC+ driver will work. (maybe)
Your AIC is not a protocol converter, its a interface converter (RS232 to RS485) and an isolator.
Your best bet would be to get a 1747-UIC ( USB to DH485 converter)for the PC connection.
Or use a memory card to program your PV.
Here are the available drivers I have currently in RSLinx. If I get the 1747-UIC will I need a different driver still?
*Maybe it's the one that says DH485 UIC devices...
Thank you both, boss will have to purchase the UIC to go forward then it looks like.
Sorry to jump in here but the best time to buy it is when you see it.
I have always used "RS232 DF1 Devices" driver with the UIC (at least with my UIC from A.B., haven't tried the other one yet).
It always auto configured fine and would insert DH485 into the Driver Config Title automatically.
:confused: At what point do we need use the "DH485 UIC Devices Driver"?
Just curious for my own knowledge as I have not needed to use it in the past with the UIC.
Thanks in advance for any input.
BCS
Either one will work fine, RSLinx "UIC Devices" and other drivers are not included (or) installed on a 64bit PC, when RSLinx installs the software first detects what the OS is on the PC then installs only whats supported (this is RSLinx about 2.54 and newer) there are a few drivers that will not work so they opt-out of installing them, helps with fewer tech support calls
But both DF1 and UIC devices work great and I have not see a issue with using either one, the only parameter to set in the UIC is node and COM, so its easier to setup for most people
This may have changed with newer RSLinx but thats how it was
I have a G306 hmi I have tried to upgrade from a panelview 600 on an existing line that is connected to a SLC 5/03. I have had succuess for the...
2,605
I want to download SLC 503 using DH485 port but I did not have 1784-PCMK card and cable. I could not use com port of processor because it is used...
2,983
Hello all. I would appreciate your help in troubleshooting an AB multi-drop DH485 network. Our company was retained to modify existing machinery...
7,305
Hello, I have a Powerflex 40 with a 22-COMM-E module and its connected to 3 Powerflex 4 over RS485. Its address is 192.168.1.25. Is it possible...
1,391
I need help setting up Modbus RS485 communications between a Red lion G307K200 and an Advantech Adam 4168 to both read and or force the output...
3,947