Bit_Bucket_07
Member
I wasn't referring to how fast the PID updates. I was referring to how short the integrator time constant can be and not oscillate. If the integrator time constant can be 3 to 5 times shorter or faster than the time constant for the disturbances then the error should never exceed 1%.
The update time of 100 millisecond seems to be plenty fast enough. I am assuming there is 12 second between divisions on the trend. The current integrator time constant is 10.5 seconds. The disturbance seems to occur over about 6 seconds before the integrator winds up to correct. What if the integrator time constant is set to 2 seconds? Now the integrator may be able to wind up faster than the error can deviate 1%. The valve should be able to change that fast.
Yes, well I wasn't referring to this particular PID's tuning whatsoever, but to the fact that a PID controller (in general) is capable of being tuned to respond quickly enough to react to such extreme transient deviations. That said, generating the appropriate response mathematically means very little if one's control equipment is incapable of responding as quickly as does one's microprocessor based PID algorithm.