Digital Panel Meter with Kepserver

vel_sathish

Member
Join Date
Feb 2007
Location
Tamilnadu
Posts
15
Hi all,

I have one digital panel meter (L&T make, Quasar Type) connected with PCthro kepserver interface. The datas recd from the meter is having 10 digits in kepserver. But in the meter it is showning some voltage valus like 85.5 or 90V like that. Can anybody help me to convert the 10 digit value to the above value in order to display the value in SCADA.

Note : In kepserver i have configured as Double Word & the protocol will be Modbus RTU.

Regrds,
sAtHiSh
 
If you double click a tag in Kepware you'll get a property window. By default the general tab will be selected. Select the scaling tab. You can choose your scaling type and range. Selecting a data type like "Short" for the scaled value range may cut off some of the precision. You might also need to round the value prior to displaying it in your HMI package.

vel_sathish said:
Hi all,

I have one digital panel meter (L&T make, Quasar Type) connected with PCthro kepserver interface. The datas recd from the meter is having 10 digits in kepserver. But in the meter it is showning some voltage valus like 85.5 or 90V like that. Can anybody help me to convert the 10 digit value to the above value in order to display the value in SCADA.

Note : In kepserver i have configured as Double Word & the protocol will be Modbus RTU.

Regrds,
sAtHiSh
 

Similar Topics

I have a requirement to provide and install digital panel meters in a cabinet I am supplying. Specifically, they must be NEMA 4X and UL 508...
Replies
5
Views
8,150
Hi everyone, I'm looking for a "digital panel meter" type display that is capable of displaying a value from a CompactLogix PLC over EtherNet/IP...
Replies
7
Views
7,184
I have a project for which the specifying engineer has called out four panelmount 3 1/2 digit LED digital numeric indicators to be mounted on the...
Replies
13
Views
7,517
Question to anyone with ideas about my thoughts on upgrading a very vintage timer, which is being used to switch between 2 5hp domestic water...
Replies
14
Views
442
I have a PLC type PM856 from ABB with some I/O modules and I get an error from the Digital Inputs model type DI801. The unit status shows error...
Replies
0
Views
268
Back
Top Bottom