Directlogic PLC output troubleshooting
zacherypost
Jan 2020
Lehigh Valley, Pennsylvania
Hello everyone,
Background: We have a Directlogic 405 PLC that has an output card that has all solenoids on it. These solenoids are on plugs with LED indicators showing their state. It is a Triac based output card D4-16TA
The problem: All the solenoids on this output card have their LED illuminated showing an on state when they should be de-energized. A voltage test shows 16VAC from output to neutral. When the output gets energized, the solenoid does not change states. DMM shows 130VAC to neutral in this state.
Failed solutions: We have swapped the output card and changed the PLC backplane. I've added resistors up to 30kohms in series and parallel. Relanded every neutral on the terminal block strip. What else should we be looking for?
Any help will be greatly appreciated.
Yikes. The solenoid coils should have sufficient draw to pull down the leakage without adding resistors, so your LEDs should NOT be lit. Many times, indicators behaving "funny" can be caused by a problem in the common return connection, be it AC or DC. Solenoids not changing state also points to a connection problem. I would only suggest, to make sure that your plug-in connectors and coils are properly wired internally AND connected back to neutral. And your terminal strip also is actually connected back to the neutral, no missing or loose jumpers. Stuff happens. :D
simple test would be to jumper from know good source to output terminal(120VAC), does solenoid work? if it does not then either a neutral problem or bad solenoid.
If it works then you have a problem with output. To check output common 120 vac find know good neutral and measure from there to output common power source, if that measures good then you have a problem with output card or PLC
Quick update. The equipment had an hour of d/t today. I swapped the PLC output card and terminal block and the problem continues. Disconnected an effected solenoid jumper from known 120vac source to isolated solenoid, and solenoid fired. Hmmmm(n)
Good morning fellow sea captains and wizards, I am being asked to do the above and obtain 4 values from each slave, I know about the MRX and MWX...
32
833
Can someone please explain the sinking and sourcing with respect to DL405 series PLC? I have already been through the manuals. Explanations with...
1,999
Hi, I'm new to DirectLogic PLCs and I need to know how to determine how much of the PLCs memory my program is using. Can't seem to find it in any...
2,041
Dear fellow Experts :), I would like to know if anyone was sucessfully in communicating to: DirectLOGIC remote I/O rack (EBC - Ethernet Base...
2,242
Today I ran into something I have not seen before. I downloaded the program and of course there was no documentation. I seen a timer or TMRF with...
1,879