Do I need a shielded wire for 4-20mA signal?
Cryogen
Oct 2005
NH
151
I have a SLC 500 PLC with NI4 analog input card. I am using two 4-20mA signal coming from an RTD transmitter. The overall length of the cable is around 20ft. I have very limited knowledge in grounding and shielding. In my understanding, voltage signals are more susceptable to interference than current signals. So I am not sure if we need a shielded cable for this signal..
Please let me know what I should do.. Any documentation on basics of grounding/shielding would be helpful too..
Thanks for your time!
I would use shielded cable. Even if you don't have interference from any other source NOW, you might in the future from a new/changed process requiring components that would interfere with non-shielded wire.
Download this document from mrplc.com: EMC Guide
Help with selecting shielded cables:
Chapter 2 - Cables
Advice on termination of shielding:
Chapter 2 - Wiring Rules
Thanks for your replies.. It would definitely help me..
krk, I created a login on that site but still it doesn't let me download anything.. says
You Do Not Have Permission To Download Files In This Category
What should I do to see the files?
Thanks..