Does AB 1734-EP PS occupy a slot in CLX IO Config?

wildswing

Member
Join Date
May 2005
Location
Sault Ste Marie, Ontario
Posts
281
Hey fellas,

I've got a 1734 PointIO system that contains a few 1734-EP booster supplies mixed in with the other IO modules. When doing my IO configuration in RSL5000 (CLX L55) do these extra PSs occupy a slot number, or do I configure the IO modules as if the PSs weren't there?
 
On a POINT backplane, the 1734-EP24DC and -EPAC and -FPD modules do not communicate on the bus or take up a Slot number.

Only the Adapters (1734-AENT, -ADN, -ACN15) and POINT modules themselves have Slot numbers.
 