downloading AB Data Table only
gregi
Oct 2008
illinois
17
can I download a Data Table only to existing PLC program (SLC5/05)and vice versa program only without destroying Data Table?
No.
Allen-Bradley controllers have always considered the data tables to be part of the user program and there is no "partial download" feature. That's just the way they work.
One workaround is the Tag Upload/Download Tool that uses RSLinx as an OPC server to bulk upload data table values to a PC and then bulk download them to the controller. This can serve as a "preservation" method for data that has been developed over time in the control system.
This tool is included with RSLogix 5000 (installed into the RSLogix 5000 Tools folder) but can also be obtained from RA separately.
That program works with MicroLogix, SLC-500, PLC-5, and ControlLogix/CompactLogix controllers.
It does require a licensed edition of RSLinx Classic, because it uses OPC.
Partial download of program and data files is available for the PLC5's. Should have been made available for the SLC's.
This may give you what you want:
http://sourceforge.net/projects/abdf1/
It allows you to upload data tables and save them to a text file, which can then be downloaded back to the controller separate from the program. It's very handy if you have a program you modified offline that you want to download, but want to preserve the current data in the PLC.
When I upload a program from one S7-1200 then download it to another I always end up with all zeros for the M registers. Is there a way to...
1,454
PowerFlex 525-Getting"Data Value Out of Range"when downloading in Drive Tab in 5000 Good Afternoon , I started a thread last week. I am...
4,174
Hello all, Newbie in Siemens, I want to ask if there will be any issue when I download the instance datablock of a certain Function block? Also...
4,443
Question on Step 7. If you download a Data Block, Do you need to upload first to have the current values before downloading? An example is if...
2,391
I have a need to enter ~36,000 data points into the data tables N200...N255 on 10 different PLCs (SLC 5/04). I have all the data points in excel...
2,178