Drive Questions
arocon
Oct 2006
Dubai
171
Two questions regarding sinamics s120 drive with sensorless vector control for ac induction motor
1) If i increase inertia of the motor, does speed acceleration will increase ? How can i find out what relation between motor inertia to speed acceleration ?
2) If i put proportioanl value for speed controller or current controller very inappropriate could it cause motor damage ?
Thank you.
These look like homework questions.
This is more of a physics question than a drive question. if you increase the inertia will it require more or less power to accellerate?
Think about what effect increasing these gains might have? What is the consequence of setting any control loop gain too high?
Nick
I think it is mostly a drive question. The answer is that, within the torque and current limits of the motor/drive system, changing the inertia of the rotating machinery will not change the acceleration rate. When you program a specific accel/decel ramp into a VFD, it will force the motor to follow the ramp until either the torque or current limit is reached. At that point, either the drive will stop accelerating until the torque or current comes down or, if electronic shear pin action is active, the drive will fault and coast to a stop.
Hi all, I have a project that use 755 drive to control a induction motor(pump) to maintain certain flow rate. Flow meter is promass 100, unit is...
2,287
Good evening gentlemen. I just want to start off by saying that I have learned a lot by reading these posts just about every day. But I have two...
2,776
I am replacing a US Drive VFD with an Emerson 201m VFD and this is the first time I have ever installed one. I have it working so far in keypad...
1,210
We use sinamics S120 with CU310 for conveyor system of rollling mill(to tranport steel coil). The system use sensorless vector control ? During...
1,760
Anyone please tell me the name of a book for rolling mill drives. It should include how to calculate drive ratings and accelerate and declerate...
1,081