I am not familiar with calculating the resistance value for a DBR. What resistor would I need (ohm + wattage) for a 90vdc, 7.5A, 3/4HP baldor cdp3443 using the kbic 125 speed control?
I usually size the DB resistor so the maximum braking current is about 150% of the motor full load current. 150% of 7.5 amps = 11.25 amps. The resistance value is 90v / 11.25A = 8 ohms. The peak wattage rating of the resistor would be 90v x 11.25A = 1012 watts. However, since the brake will not be on continuously, the resistor does not have to be able to carry the 11.25 amps continuously. Depending on how often the motor is stopped, a duty cycle of 5-10% could be used. Most resistor manufacturers have graphs for rating their resistors for intermittent duty. You could probably use a 150 watt resistor for this application.
The answers given the OP in this thread are valid for maximum possible braking only. The first key question when dealing with braking is to determine how much braking IS REALLY NEEDED. It could be more than the motor hp or even much less. That's the resistance value you need.
In my experience, I've encountered braking applications where the braking hp is 1/10 of motoring hp and on one occasion where the braking hp was 4 times the motoring hp. In that case, the drive and motor had to be sized to the braking rather than the motoring hp.
I have a vector drive faulting out. Manual says inspect and test the Braking Resistor. I have never done this procedure before. === From...
2,765
How should I select the Ohm value and power rating for a dynamic braking resistor? This DBR will be used in a DC Converter that supplies 680 VDC...
5,557
I haven't done many applications with braking resistors, but we just put one in for a customer on a 60HP application for a centrifuge. We're...
21
6,467
I have a customer who has a centrifuge application. The plant engineer did all the calculations on the centrifuge to arrive at a WK^2 of 6458...
3,593
I have a bit of an in-depth question on the operation of dynamic braking / regen. What I know and please correct anything that I am incorrect...
2,396