I have attached the circuit diagram of the cylinder. I'm open for suggestions on how to exhaust air from the cylinder or move piston back to original position when E-stop is pressed.
 
ashika,

I STRONGLY urge you to get help !!
Even with the schematic you provided, we can offer suggestions only.
I do not believe that you understand the system design and the implications of what you propose, no offense intended.

I am going to assume the sda valve is a part holding cylinder.
YB and YA appear to be backwards in your descriptions.

Is the intensifier an air intensifier or is this an air over oil type system?

if its an air over oil system, it will not move freely, the valve prevents the design from becoming air locked for lack of a better term.

if this is an air intensifier, you definitely cannot do what you want!
the air pressure stored in the intensifier is more than your line pressure.

Again, please seek the help of the oem that built the equipment.


james
 

Similar Topics

We are facing intermittent issue with emergency stop and line stop. Line stop triggering with alarm of line stop push button activated at one...
Replies
10
Views
207
Hope you are doing well. Currently, I am involed in a revamping project. It requires to stop a mixer at specific postion. For the detail, this...
Replies
9
Views
288
Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
Replies
19
Views
375
I'm looking to get some spare keys for this PLC. Does anyone know a source or have a part number? My searches are turning up nothing at the moment.
Replies
1
Views
100
Hey all, I am currently working on a depalletizer for a customer and we are doing a hoist upgrade. This is a SLC500 processor and the drives are...
Replies
6
Views
323
Back
Top Bottom