Hey Fella's,
Been asked to pull some trend data out of some EGX100 units. They are on Ethernet back to a switch, and I think they talk rs485 to the power monitor units.
Anyone have the communication settings for citect that I could use?
Is one egx100 to one power monitor.
Done plenty of Rockwell setups in the past but not this.
Anyone help get us started? cheers :)
ok, got some of this working - still have some further questions however.
The EGX 100 gateway unit is connected to a Schneider PM 3250 power monitor via rs485 / Modbus.
citect comms setup - the node number of the pm3250 was set up as #8
attachment.php
tag setup - note from the register table - needs a 4 in front of the holding register number
also had to make the following change to the citect.ini file :
[MODNET]
FloatMode = 1
attachment.php
attachment.php
attachment.php
stuff I would like to know how to do
1..on the pm3250 unit, there is a kwh totaliser (378249 value)
I cant see which registers hold that totaliser figure, and they are a 'int64' type - anyone know how to decipher that?
2..How to reset the maximum current values via citect - I assume they are for the month??
3..Is possible to collect this data using rsview32 instead if citect? Can rsview32 be used for Modbus over Ethernet??
attachment.php
attachment.php
Sorry to bump my own thread, but am desperate to get this thing going - hoping for a .ctz file I can chew on :(
It takes 4 consecutive registers as standard modbus register is 2 bytes long
Directly on power meter, through setup...
As I recall you need OPC for rsview32 and modbus, but I'm not sure. Anyway bot EGX100 and Citect are Schneider Electric, so my suggestion is to stick ti Citect.
decided to cheat and pulled the PM3250 data thru the EGX100 gateway and into a message in a micrologix 1100. Can read from the MLX from rsview32 easier that way. Will throw it into a CLX in a few weeks but good to see it working in the 500
data table / message conversions
attachment.php
don't forget in the channel configuration for channel 1, tick the box that is " Modbus TCP enable" then cycle power to the plc.
message setup and register conversion code
attachment.php
attachment.php
hope someone finds this usefull. be good if the vendors had all this info out there to begin with - anyway...
@Robbo,
I'm looking to do basically the same thing you did/are doing. I want to pull data into a CLX processor from an EGX100 that has 5 devices daisy chained via RS-485. (L61Processor-CAT6-EGX100--RS485--Dev1--Dev2--...Dev5).
I tried looking at your screenshots above for help but the resoultion isn't high enough for me to make out clearly what they say. Could you post the MSG instruction screen shot again for me, but more clearly?
I see your Modbus address is 43000. Where does the 4 come from? I see in your data tables above a few 4s, but not sure if that is merely coincidence. I'm not sure of the headers on those data tables.
Also, you seem to flip the order of the integers. Why is that?
What is the port # in the MSG instruction?
Thanks so much for the help. This is my first time working with the EGX and Modbus so your examples above have been very instructive. Looking forward to your response.
Hello everyone. can you please tell me how to connect between Rockwell PLC and EGX100 (Schneider)-connect power monitoring over Modbus. many thanks.
2,083
Hi, i am using DVP-14SS2 PLC, after program written to plc, when power is reset, plc doesn't run. always need to connect to pc for the run mode.
32
Hello all, I am currently trying to program a PowerFlex 525, version 7.0. We had a power outage recently and when the power was restored, the...
288
Looking at installing point io, with a 1734-AENTR communications adapter and ten 1734-IT2L modules. In IAB it installs a 1734-EP24DC after every...
68
First time I've used either the software or this unit. This is the setup I have right now. I have 20mA coming into AnalogIP1. Both the Main.PV...
47