Emergency Stop Pushbuttons
Oct 2016
Philadelphia, Pa
20
Hello Everyone
Had a question on emergency stop buttons
One of my customers in the oil and gas industry has multiple emergency stop buttons wired into a panel that are then wired into an SIS system. When any one of the buttons is pushed on this panel, it activates certain logic to shut down specific valve/motors associated with it. Actually, a few of those buttons shut down the plant operation, while other only shut down a few devices.
The PHA that they performed did not classify any of those emergency stop buttons as SIL rated SIF's, so they were asking me today if there were any specific ISA, IEC, PSM/OSHA or API standards that required testing of those emergency stop buttons at a specific frequency (event though they are not SIL rated SIF's). Any input that you can provide would be greatly appreciated.
Thanks in advance
It can't be an emergency stop without a SIL rating. The whole design and validation of a safety function involves the SIL rating. This includes the buttons, the logic / safety relay / outputs etc etc
I cannot understand how they have got to that conclusion. Someone has made a mistake or got things very mis-understood.
It's just a general stop button and if it is dressed as emergency stop buttons then they have some problems.
I know it puts food on the table, but I wouldn't put my name to this particular machine without some clarification first.
A good read nevertheless here:
https://machinerysafety101.com/2009/03/06/emergency-stop-whats-so-confusing-about-that/
A SIF could end up with SIL0, no SIL, depending on acceptable risk vs actual risk. The numbers should be found in the risk assesment.
Otherwise I agree with janner. Sounds weird with emergency stop as non-SIL.
Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
19
375
Hello, I have plc Schneider TM241CE40T with the hmi HMIS5T. Do you have idea how to disable a button after an emergency stop to vijeo designer ...
1,491
Dear colleagues I am learning to program siemens plc. I have a problem with how to solve the problem with a power outage and emergency STOP...
1,763
Hi, I would like some recommendations/advice on wiring of a dual channel Emergency Stop for a 240V AC motor (single phase), I have 3 options in...
47
13,886
Hi, We have a machine that we wan't to restart after power on if the emergency stop is OK. But if the emergency stop is tripped with the button...
21
6,613