Encoder Diameter Disk Calculation
Diver_Man
Aug 2002
Rio de Janeiro
How do i calcilate the diameter of the disk to be used to install a encoder ? Is there a formula to calculate the diameter of the disk ?
Lets suppouse that i would like to get 5000 pulse/m and i have a encoder that have 2500 PPR ( pulses per revolution ) so i would like to know the diameter of the disk that must be used to get 5000 pulse/m using this encoder.
I would like to know too if this is the right way to work with encoder diameter disk?
thanks,
Luciano
I assume that by a 'disc' that you are referring to some sort of measuring wheel that will be mechanically attached somehow to perform linear measurement.
You want 5000 pulses/meter
You want to use a 2500 pulse/rev encoder.
(2500 pulse/rev) / (5000 pulse/meter) = 0.5 meter/rev
This is your desired circumference. Solve for diameter
Required diameter = circumference/ Pi = 0.5m / 3.14159 = 159.155mm
It's really better to work it in the reverse order. I mean, look at what you already have, or can tolerate, mechanically, then choose an encoder resolution that will get you close to what you want in overall resolution.
I agree John. I usually look at how much resolution I need for my application (pulses/mm or pulses/inch, etc) and then choose a feedback transducer and measuring wheel that will give me my desired resolution. Typically I will try and use a commercially available transducer and then size the measuring wheel as the last issue.
I try to pick a wheel & transducer combination that doesn't result in excess speed since this can result in early bearing failure of the encoder, and there is a greater chance of 'slippage' if a smaller wheel is used.
Hello, I was hoping someone could help me out with a bit of physics. Currently I have a cart that has 5 inch (diamter) wheels on it. On the...
61
28,139
I need to monitor the diameter of a roll of paper as it winds onto a core bar. The speed is constant, the core roll diameter changes with each...
10,528
Sorry in advance for the long post, but this requires a little back story. I work in a facility with a couple hundred VFDs Most are in a web...
251
I have an application using an incremental encoder and then I convert it to degree (0-360) using calculation program. For a while, the calculation...
339
Hi everyone, This is my first time posting, so please forgive any omissions or mistakes. I am attempting to control the velocity of a stepper...
18
1,051