Error when converting from S5 to S7

taday

Member
Join Date
Feb 2006
Location
ha noi
Posts
3
Dear Friends,

This is the first time i did this work. And S5 PLC use the SINEC L2 communications,CP 524,IM308

Please give me some advices to solve this problem!

I attached with error's picture.

Thanks in advance!
 
Only works 80% the rest like those send & receive blocks have to be manually set up. There is windows Step5 software to help a little but it is going to be some hard work ahead. The siemens S7 software does not work 100%. This is a good question for the forum.
I have changed a program and ended up almost rewriting the program.
Have you googled this.
http://www.softwaretoolbox.com/store/item_pages/itempage_510.asp
 
One pitfall is if you intend to reuse the SINEC-L2.
Are there SINEC-L2 slaves attached to the IM308 ?
If so, you must be aware the initial variant of SINEC-L2 is not compatible with Profibus DP. A later variant was called SINEC-L2 DP, and it was compatible with Profibus DP.
 

Similar Topics

We just completed the conversion of a PLC 5/80 to a 1756-L8x processor. The old 5 program had numerous MSG instructions sending data to/from...
Replies
24
Views
9,558
Hello :) I've already come up with a solution to the problem described below, so this is mainly a curiosity had the situation been different...
Replies
6
Views
3,722
I have some error about RJ area on Regular PID code S5->S7 FUNCTION FC 30 : VOID AUTHOR: _48021 NAME: HAU_KREG // HAU:KREG VAR_INPUT...
Replies
2
Views
2,088
Help! I'm not too familiar with Omron. I would like to know if there is an easy way to locate where the problem is in the program? I converted an...
Replies
4
Views
7,995
Hi Everyone. Not posted on here for a long time, but I am hoping someone can help me. I am doing a differential pressure calculation in a L27ERM...
Replies
16
Views
313
Back
Top Bottom