Explosion proof PLC / HMI panel

dkpramanik

Member
Join Date
Sep 2013
Location
Dhaka
Posts
5
One of my customer asking an explosion proof HMI + PLC panel for LPG storage tank hazardous zone. The HMI to be for both controlling (by hand touch) and monitoring. The PLC and HMI must be Siemens brand.


What is the best way to do/get that?
 
Ask for the hazardous area location drawing and where they want to install it along with the risk assessment.

If it's not in a Zone 2, then can't be done.


If it's in a zone 2, contact someone that can design that for you to be certain of what you're doing.
 
I think it could be done with a rated, purged enclosure, but the HMI would have to be inside the enclosure, and you view it via window. Need to check with your local experts.

The enclosure is purged for a set period before power is applied, once power is applied, it pressure drops below a minimum value, the power is removed before explosive vapor can enter.

You want to make sure what ever system you use is approved/certified by a third party. In the US, this would be FM or other authority. It's going to be expensive.


I think it would be more cost effective to have the PLC in a safe area and use Profibus PA (intrinsically safe) for field devices. The HMI would still be a challenge.
 
Since this is out of my area of expertise, legal knowledge, and legal/financial liability I will tell the customer Sorry, I can't do it & won't take on the liability.


Since your OP states you are as experienced in explosion proof panels I suggest you do the same.


Even if you sub-contract this out to a qualified panel shop to design & install it for you it will still be your liability since you took the project on.



If you do find a qualified panel shop then tell the customer they have the knowledge and use them directly without your name on any of the contracts, sales orders, quotes, etc.
 

Similar Topics

are rigid conduits suitable for isolating electrical cables in an explosive area? it is a new factory with machines making solvent based ink. what...
Replies
16
Views
4,513
Perhaps I am asking my suppliers the wrong questions, but I need some sort of flexible cable for a 4-wire RS485 application. It is a Class 1 Div 1...
Replies
3
Views
2,724
Hi, I have a lot of doubts about this topic. Im used to perform typical automation systems using schneiders plc, altivar drives, and regular...
Replies
5
Views
2,605
I am in the process of quoting a job with explosion-proof requirements. I have been able to get everything I needed, except for the...
Replies
2
Views
3,181
Hi, Has anyone come across an explosion proof standard inverter?? In order to use the inverter in explosion proof environment, I think we've...
Replies
17
Views
7,027
Back
Top Bottom