OT: Explosion-Proof Signal Cable
J E
Jan 2007
Louisiana
53
Perhaps I am asking my suppliers the wrong questions, but I need some sort of flexible cable for a 4-wire RS485 application. It is a Class 1 Div 1 environment. It is a short run, and it is hard to justify the expense of isolation barriers. Can anyone make any recommendations?
J E,
if this is a class 1 div 1 environmnent, then you have no choice but to use a barrier. The NAtional electric code (NEC 70) sections 500-5?? defines hazardous installation requirements.
from your safe area, you will need a barrier, then rigid conduit to within 18" of the hazardous wall, a seal, and continue on to the end point in rigid conduit to your device.
the installation requirements should have been spelled out by the engineer classifying the area.
regards,
james
One advantage of Intrinsically Safe implementations in hazardous areas is that the wiring does not have to be EXP.
RS-485 can be made intrinsically safe as evidenced by Profibus DP's use of RS-485.
But all the components of an I/S installation must be certified and transitions from safe to hazardous areas need to an appropriate barrier.
Unless the RS-485 on both ends has a control drawing for I/S, you're stuck with the rules and regs of explosion proof.
501.10(A) allows for other methods besides rigid conduit without requiring a barrier or an intrinsically safe installation for Class I Div 1, notably the use of MC-HL (for power applications) and ITC-HL (for instrument applications). The designation "-HL" refers to Hazardous Location.
You will have to do a cost comparison because the cable glands aren't cheap, but neither is the barrier (we use Stahl Type 9185 Fieldbus Isolating Repeater - around $1500 each).
However, the use of MC-HL and ITC-HL are restricted to use in "industrial establishments with restricted public access, where the conditions of maintenance and supervision ensure that only qualified persons service the installation" among other conditions such as using the required listed termination fittings and proper sealing at ALL ends/terminations.
Okonite has an ITC-HL cable made for Fieldbus applications. It is 18AWG and comes in 1 to 24 pairs, so you "may" be able to use a 2-pair for your RS485 depending on what you want the second pair for (for a 4-wire application, or as a power supply to the RS485 device).
I would call Okonite to check on the suitability for RS485 comms for a short run.
http://www.okonite.com/product_catalog/section5/section5-pdfs/5-48.pdf
Crouse-Hinds listed exp sealing gland:
http://www.cooperindustries.com/content/dam/public/crousehinds/Industrial%20EX%20Products/Catalog%20PDFs/Fittings/ADE%206FC%20Armoured%20Barrier%20Gland_North%20American.pdf
PLEASE review NEC 501 in reference to allowed wiring methods (501.10A for CID1), the allowance for using ITC-HL cables, cable sealing, and article 725 by reference.
One of my customer asking an explosion proof HMI + PLC panel for LPG storage tank hazardous zone. The HMI to be for both controlling (by hand...
3,243
are rigid conduits suitable for isolating electrical cables in an explosive area? it is a new factory with machines making solvent based ink. what...
4,524
Hi, I have a lot of doubts about this topic. Im used to perform typical automation systems using schneiders plc, altivar drives, and regular...
2,615
I am in the process of quoting a job with explosion-proof requirements. I have been able to get everything I needed, except for the...
3,182
Hi, Has anyone come across an explosion proof standard inverter?? In order to use the inverter in explosion proof environment, I think we've...
17
7,034