Hi Guys!

I was wondering whether you know of a non-painful way to check whether all the tags used in a FactoryTalk RSView project are broken or not?

We have several people working on the PLC and the HMI.
Sometimes, PLC guys change tag names without knowing it is referenced by HMI.

Is there a way to check whether all the HMI tags to PLC are still intact?

Thanks!
 
You might try the ADLauncher.exe utility in FT View. This is the Application Documenter tool, it has a tag cross reference feature that I have found useful before.
 
Yeah, i found that Application Documentor quite helpful as well.

It listed out all the Tag references references, which is good.
But it doesn't quite tell me whether or not that tag is valid.

I'm hoping to detect the case where an HMI button refers to {::[PLC Local]Program:Module1.SomeVariable} but PLC does not have that variable name.
 
Refers to RA knolwdgebase. TN = Technote. You will need a contract to view the TN. But the utility only works for HMI tags, not direct referenced ones. I don't know of a utility for direct referenced ones. I know tags that FTView can't find are logged to the diagnostic log. Try loading every screen, usually if a tag can't be found on the display, FTView will tell you.
 
Thanks!

I think it is possible in FactoryTalk View Studio click "run" for each page.
It will help pick up some errors broken links, though not all of them.
 

Similar Topics

Hello everyone, I am having a problem with conversion from RSView32 to FT View SE Local project on version 12.00 (CPR 9 SR 12). Firstly, I have...
Replies
6
Views
1,409
Hello, I need to prepare a brief write-up of the history of FactoryTalk. I've gathered that it is from and built upon RSView/RSView32, but...
Replies
7
Views
2,947
Hello! I am currently working on a migration and I need to migrate a ControlView application to FactoryTalk View, reviewing some manuals I have...
Replies
5
Views
1,824
Hey everyone, I know that this might seem a little backwards, but my company runs machines with HMI's in RSView and more recently, FactoryTalk. I...
Replies
1
Views
1,763
I know PLCs, but I usually work with Wago or Siemens. Our customer has specified Allen-Bradley for this current assignment. I received the AB...
Replies
6
Views
6,990
Back
Top Bottom