Fault 0301 (Out of buffer memory) on 1756-ENBT

sanger

Member
Join Date
Nov 2005
Location
Toronto
Posts
172
We've been getting this fault intermittently on a 1756-ENBT module. PLC needs to be powered down to reset it. The ENBT module revision is 4.8.

There is no PLC to PLC communication on the Ethernet but there are 3 SCADA systems reading/updating approx 200 tags each on the processor at 200ms update time. We have a system next to it that is running with no problems. The second system is identical except that the ENBT module is revision 4.3.

Any ideas.
 
I had a similar problem...
The ENBT was one of the products effected by the Atmel ASIC chip recall.
Look from the top of the card and there is a large chip and if the make is Atmel and the two numbers at the end of the next line read 64 you're in trouble.
Look at for Tech Note ID 41204 for more info.
 

Similar Topics

Hi All, I'm getting the following error on the 1794-OB16P/A module: Module Fault (Code 16#0301) Connection Request Error: Out of buffer memory...
Replies
1
Views
8,407
All, I have a PowerFlex 525 driving an agitator motor. The goal is to have the agitator start automatically after a power loss or a comm loss. I...
Replies
2
Views
74
hello I am getting a 57h fault - Specialty I/O module has not responded to a lock shared memory command within the required limit. Fault randomly...
Replies
2
Views
95
Kindly, we have the following configuration fault on a Kinetix 5700 axis. It only appears when we go online on the Plc. We are just starting the...
Replies
2
Views
102
Have a system that has been running for over a year and all of a sudden getting a ExcessiveVelocityFault on one of the drives when the MSO command...
Replies
2
Views
156
Back
Top Bottom