Fault on a Micromaster 440 with Profibus adapter

I had a few drives give this fault before.
F0022 (Power Stack Fault)

Most times you could reset the fault and the drive will sputter along happy as a clam afterward.

But we did have 3 drives that never recovered from this, they locked out on F0022 and no matter what you did they would not budge.

We changed the I/O board, checked all wiring and grounding, disconnected motor leads and tried to run, all these are what the manual says to try.
Non of these things worked.

Changed out the drive and new drive worked just fine on same cable and motor.


Sent drives in for repair, and got quote of 2/3 what a new drive would cost so we just elected to purchase new drives.

Not much help I know but that is my experience with this fault.

Good Luck

BCS
 
We changed the drive out and away we went. The drive control power which was suppose to be 24volts was down to 18volts
 
Thanks for posting that.

Next time I get this fault I will check the same, and then see if the drive will work using an external power supply.

I have lots of Siemens 440 drives in operation some using onboard control power and some using external control power.

Maybe I can find a home for some of these if that is the only problem they face. Power supply is much cheaper than a drive.

BCS
 

Similar Topics

in allen bradley kinetix 300 drive first E31 error shows after resting drive E11 error occurs need solution to reset E11 fault code
Replies
0
Views
16
All, I have a PowerFlex 525 driving an agitator motor. The goal is to have the agitator start automatically after a power loss or a comm loss. I...
Replies
2
Views
88
hello I am getting a 57h fault - Specialty I/O module has not responded to a lock shared memory command within the required limit. Fault randomly...
Replies
2
Views
98
Kindly, we have the following configuration fault on a Kinetix 5700 axis. It only appears when we go online on the Plc. We are just starting the...
Replies
2
Views
115
Have a system that has been running for over a year and all of a sudden getting a ExcessiveVelocityFault on one of the drives when the MSO command...
Replies
2
Views
159
Back
Top Bottom