I received this private message from sevensages:
"plzz advise to construct a fip io architechture with momentum i-o & premium plc"

Fipio fieldbus is a means of communicating between different components. Up to 128 devices, from different manufacturers, can be connected. It is based on World FIP producer/consumer standards. Total remote I/O length can be up to 15km. The standard cabling is 150ohm twisted pair with fibre optic as an option. Devices are connected to the bus by daisy-chaining or via a trunk line with tap connections.

The Premium PLC TSXP57?54M, with an integral Fipio port, will act as the fieldbus manager. A TSXFPACC12 cable is used to connect the PLC to a TSXFPACC14 connection box. The PLC program treats the remote I/O the same as "in rack" I/O. I/O scanning is periodic and deterministic.

The Momentum I/O blocks require the 170FNT11001 communication module. A TSXFPACC2 cable is used to connect the I/O to a TSXFPACC4 connection box.
 

Similar Topics

Hi, I have a machine which uses FIPIO to communicate between a TSX Premium under PL7 and ATV58 drives. The cable needs replacing but the...
Replies
5
Views
2,987
Hello All, I am stumped on how to convert a %MW to a %MF using Machine Expert Basic and a Modicon M221. The help files show a word to a double...
Replies
4
Views
122
Hi, Is Control Expert V15.0 supposed to support multiple monitors? I'm running Control Expert V15.0 on my host Windows 11 PC, connected to two...
Replies
1
Views
67
Everything was working fine, but suddenly CPU went into error mode, and the ERR and TER LEDs lit up. Now I can't download or connect with the PLC...
Replies
0
Views
84
Hello all, I am wanting to update the system clock via NTP in the M580/M340. I'm aware that we are able to connect to a NTP in the controller...
Replies
4
Views
173
Back
Top Bottom